    Can a kitchen counter outlet that's dedicated with a 12/2 be protected with a 20 amp breaker but still have a 15 amp duplex receptical.
    Thanks

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    14-600 prohibits what you described, but says,"except as permitted by other sections of this code."

    I think if there were any exceptions, they would be found in Rules 26-700 to 26-726, but I don't see any.

    26-726 specifically states that the 5-20RA (20 amp) receptacle be installed when 20 amp circuits are used for kitchen counter work surfaces.

    Ed

  3. #3
    Inactive Member Ellement's Avatar
    Join Date
    January 9th, 2003
    Posts
    53
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks once again for you informative input.

    I was unsure as I have a ref. to the NEC code that states:

    NEC 210.21(B)(3) permits either 15- or 20- ampere receptacles on a
    20-ampere rated circuit supplying two or more receptacles. However, a
    single receptacle on an individual branch circuit must have an ampere
    rating not less than that of the branch circuit. NOTE: this must be a
    single receptacle and not a duplex or greater.

    I know the CEC is not the same as NEC but just curious as to the different rules.
    Thanks again.